Leader

Collapse

Announcement

Collapse

Firehouse.com Forum Rules & Guidelines

Forum Rules & Guidelines

Not Permitted or Tolerated:
• Advertising and/or links of commercial, for-profit websites, products, and/or services is not permitted. If you have a need to advertise on Firehouse.com please contact sales@firehouse.com
• Fighting/arguing
• Cyber-bullying
• Swearing
• Name-calling and/or personal attacks
• Spamming
• Typing in all CAPS
• “l33t speak” - Substituting characters for letters in an effort to represent a word or phrase. (example: M*****ive)
• Distribution of another person’s personal information, regardless of whether or not said information is public knowledge and whether or not an individual has permission to post said personal information
• Piracy advocation of any kind
• Racist, sexual, hate type defamatory, religious, political, or sexual commentary.
• Multiple forum accounts

Forum Posting Guidelines:

Posts must be on-topic, non-disruptive and relevant to the firefighting community. Post only in a mature and responsible way that contributes to the discussion at hand. Posting relevant information, helpful suggestions and/or constructive criticism is a great way to contribute to the community.

Post in the correct forum and have clear titles for your threads.

Please post in English or provide a translation.

There are moderators and admins who handle these forums with care, do not resort to self-help, instead please utilize the reporting option. Be mature and responsible for yourself and your posts. If you are offended by another member utilize the reporting option. All reported posts will be addressed and dealt with as deemed appropriate by Firehouse.com staff.

Firehouse.com Moderation Process:
Effective immediately, the following moderation process will take effect. User(s) whose posts are determined by Firehouse.com staff to be in violation of any of the rules above will EARN the following reprimand(s) in the moderation process:
1. An initial warning will be issued.
2. A Final Warning will be issued if a user is found to be in violation a second time.
3. A 3-day suspension will be issued if the user continues to break the forum rules.
4. A 45-day suspension will be issued if the user is found to be a habitual rule breaker.
5. Habitual rule breakers that have exhausted all of the above will receive a permanent life-time ban that will be strictly enforced. Reinstatement will not be allowed – there is no appeal process.

Subsequent accounts created in an effort to side-step the rules and moderation process are subject to automatic removal without notice. Firehouse.com reserves the right to expedite the reprimand process for any users as it is deemed necessary. Any user in the moderation process may be required to review and agree to by email the terms and conditions listed above before their account is re-instated (except for those that are banned).

Firehouse.com reserves the right to edit and/or remove any post or member, at any time, for any reason without notice. Firehouse.com also reserves the right to warn, suspend, and/or ban, any member, at any time, for any reason.

Firehouse.com values the active participation we have in our forums. Please ensure your posts are tasteful and tactful. Thank you very much for your cooperation.
See more
See less

2nd in engine setup?

Collapse
X
  • Filter
  • Time
  • Show
Clear All
new posts

  • L-Webb
    started a topic 2nd in engine setup?

    2nd in engine setup?

    The other tread on long drive ways got me curious about how other depts setup the 2nd engine if that engine forward lays from the hydrant to the scene.

    We had a house fire about a month ago that was a mess. A little back ground on this dept, this is a part time gig where there is only 1 24 hr and 1 12 hr day person rest are volleys, the 12 guy is at another station. I was 1st in engine the chief got on scene, gave report, called for mutual aid and advised me to come up to the house and the 2nd in could lay the line. The driveway was long but not crazy 800' or so. So.... get up to the house which is a 2 story 2500 sq ft or so about 30% involved but had yet to breach the roof. Chief is dressed out so get him a line on the ground and get water w class A foam in it, pull another line to the rear and I start hitting it from there. So there was a brief span of time where we could have gotten on top of this until....

    The 2nd in engine hooks to the hydrant and lays a single 3" up to the scene gets out and breaks the line, then he runs a 50ft section from his truck to mine?? So I'm guessing that his plan was to feed my truck from his which is fine I reckon. The problem arose when he got confused trying too be to fast and called for water too soon and charged the supply bed, shortly thereafter I ran out of water and we burnt the place to the ground.

    In hind sight it would have been better for me to take the time to get out wrap the hydrant and lay 5 inch up to the fire and the 2nd in could have made the hook up and charged the line. Also double 3s should have been laid being 800 ft long and should have IMO hooked them directly to the engine that was already attacking the fire. We had supply issues with the single 3, we set up a blitz gun but didn't have enough volume to run that and 2 1.75 lines. "" Which that has been fixed, The truck that was 2nd in now has 1000 ft 5 inch.

    So having rambled all that out, Do you hook to your engine and feed the attack pumper or break the line and hook it directly to the attack pumper

  • kuh shise
    replied
    L-Webb: Let me start by saying that we have NOT used 3" (with 2 1/2" couplings) since the mid-1980's. When we did use it, it was loaded in a split bed of 800 ft. per side, and you always (SOP) laid duals. We never adhered to the "Secure your own water" philosophy, because we were operating three stations with an engine out of each station. This allowed us to work like a "Two Section" engine company with attack and supply duties. 750 gal tanks allow an initial hit from the exterior, and then advance on the seat, while the supply is being laid. Using this technique minimizes the free burn time, and makes the initial hit in as short a time as possible. Just considering the old fire spread rate of 2x every three minutes, and if it takes an additional 3 minutes to line in, you have just halved your needed water application. Yes, waiting for the second section to lay the line poses a possible safety consideration for the attack crew, but remember some of the line laying and hook-up is now being done simultaneous to the attack lines being advanced. Taking a look at this from the water supply angle. If the hydrant supply is capable of 1,000 gpm, at 20 psi and a static of 80 psi, the 500 gpm point will be at about 60 psi. On a single lay of 3" (2 1/2" couplings) 60 psi would supply 275 gpm (friction loss formula) Dual 3's then would supply 550 gpm. However using the 2 section company with duals, the entire 1,000 gpm would be available by relaying. If something should happen to either engine, the 3rd arriving picks up the failed engine's position, or is used to supply the 4th arrival (aerial) or works the rear of the structure. If you are operating with 4" supply the numbers for the forward lay would be almost exactly the same as the dual 3". For 5" supply 40 psi residual (about 800 gpm) would get you 800 gpm with 10 psi remaining on the compound. Taking a look at needed water ( 1 3/4 = 150 gpm & 2 1/2 = 250) So two 1 3/4's and a 2 1/2 need 550) then with a forward lay of a single 3" you will only have (maybe) two 1 3/4" lines with no back-up. The 3" duals will get you two attack lines and the back-up. A forward lay single 5" will provide two 1 3/4 and two 2 1/2's. The two section with a 5" supply will provide two 2 1/2" lines plus a 1 3/8" aerial stream at 500 gpm. My son has a huge house of 5,800 sq ft, and it only requires about 700 gpm. Most residential fires will not require more than 500 to 800 gpm. Is there a risk with a 2 section company ? Absolutely, and the I.C. will need to control the attack crew until the supply is established, but there are benefits to taking the heat out of the fire. Hope this provides a different view of the problem.

    Leave a comment:


  • johnsb
    replied
    First off, I'd NEVER lay a 800' 3" supply line. At the most, we may supply another nearby piece (100' or so) with a 3" line. I'd have laid in the 5", and let them supply water to you. As for using a clamp, other than a closet in a firehouse, I've never seen one actually used in this area. As soon as the supply line is broken, it's hooked to the inlet. Most everyone around here has been using 5" for some time now, only one has 4".
    In the city, typically the second engine's job is water supply, unless they are coming from quite a distance away, or it's already a large fire calling for master streams.

    Leave a comment:


  • Skojo
    replied
    Originally posted by RFDACM02 View Post
    We do forward lay to our tower ladder which has no pump and needs the pressure boost.

    I think this is a good and important point to bring up. Our MA company runs with a tower ladder w/o a pump that requires its own dedicated truck/water supply. Just another reason (in my opinion) to have 1 rig on scene with its own dedicated line.

    Leave a comment:


  • tree68
    replied
    Originally posted by FyredUp View Post
    We do not have 2 rigs next to each other operating off the same line at the scene.
    We shouldn't, but it happens with overenthusiastic MA departments.... It's gotten better.

    Leave a comment:


  • FyredUp
    replied
    First due lays in if smoke or fire showing on both of my current FDs. If nothing showing go in and investigate, second due can forward or reverse lay depending on distance. We do not have 2 rigs next to each other operating off the same line at the scene.

    Leave a comment:


  • RFDACM02
    replied
    Our policy is if you lay a line, the first thing you do upon exiting the cab is set a clamp on the line, no charged beds, no worry of charged line flowing free. I would think knowing it was a driveway, I'd have asked the first due to lay-in. Having the second due lay in may work if your crews know how to quickly supply the first due. Where we are street-side (residential fire) I like the first due come to the scene and begin attack from the booster tank, the second due then either reverse lays (where >800 ft) or forward lay for lesser. This allows the engine to pump the hydrant for longer lays or just put the 5" direct into the first due's intake on shorter lays. I don't see value in having to pumpers side by side being supplied via the same line (ie: forward lay second due receives and pumps to first due?) just more mechanics between the supply and the firestream. We do forward lay to our tower ladder which has no pump and needs the pressure boost.

    Leave a comment:


  • Too_Old
    replied
    While first and second engine have some differences, the basic setup is the same. 1500ft of 4in supply line, 2 crosslays, 1 bumper line, 1 'long line' off the bed.

    First due engine lays out.
    Second due engine picks up the supply line and sets up the pond once the first tanker shows up.

    All the tankers have fire-pumps, so if a tanker beats the second engine, they may nurse via the supply line until the second engine shows up to establish the water supply.

    Leave a comment:


  • tree68
    replied
    Even though 800' off the hydrant is going to give you good flow, I think I'd prefer to lay in with the attack engine and hold the 2nd due at the hydrant. If there's a good IC already on scene, he/she will direct the first due to lay in.

    In our case, a pumper at the end of the driveway is mandatory, as we have zero hydrants, so it'll be drafting from the portapond.

    One problem with the second engine coming in is that invariably they'll want to pull a line off that rig, too, rather than pull another line off the 1st due. The beauty of MA and free-lancers. On top of that, they'll expect to connect to the supply line, then feed the 1st due from there.

    One consultant I know of feels there should be preconnects up to and including the max flow of the pump. I don't normally see us reaching that point of deployment at a rural fire, but it's not a bad idea. If you'd dropped the 5" with the 2nd due at the hydrant, and, using our pumper as an example, you'd have been able to pull 2 x 1.75" with fog nozzles (crosslays), a 1.75" with a straight tip (bumper line), and a 3" with a fog nozzle, all without touching a coupling, if you will. And there's enough hose in the bed to set up the Blitzfire, too.

    I would opine that whoever decided to drop a single 3" needs a refresher in hydraulics and fire flows.

    Leave a comment: