Leader

Collapse

Announcement

Collapse

Firehouse.com Forum Rules & Guidelines

Forum Rules & Guidelines

Not Permitted or Tolerated:
• Advertising and/or links of commercial, for-profit websites, products, and/or services is not permitted. If you have a need to advertise on Firehouse.com please contact [email protected]
• Fighting/arguing
• Cyber-bullying
• Swearing
• Name-calling and/or personal attacks
• Spamming
• Typing in all CAPS
• “l33t speak” - Substituting characters for letters in an effort to represent a word or phrase. (example: M*****ive)
• Distribution of another person’s personal information, regardless of whether or not said information is public knowledge and whether or not an individual has permission to post said personal information
• Piracy advocation of any kind
• Racist, sexual, hate type defamatory, religious, political, or sexual commentary.
• Multiple forum accounts

Forum Posting Guidelines:

Posts must be on-topic, non-disruptive and relevant to the firefighting community. Post only in a mature and responsible way that contributes to the discussion at hand. Posting relevant information, helpful suggestions and/or constructive criticism is a great way to contribute to the community.

Post in the correct forum and have clear titles for your threads.

Please post in English or provide a translation.

There are moderators and admins who handle these forums with care, do not resort to self-help, instead please utilize the reporting option. Be mature and responsible for yourself and your posts. If you are offended by another member utilize the reporting option. All reported posts will be addressed and dealt with as deemed appropriate by Firehouse.com staff.

Firehouse.com Moderation Process:
Effective immediately, the following moderation process will take effect. User(s) whose posts are determined by Firehouse.com staff to be in violation of any of the rules above will EARN the following reprimand(s) in the moderation process:
1. An initial warning will be issued.
2. A Final Warning will be issued if a user is found to be in violation a second time.
3. A 3-day suspension will be issued if the user continues to break the forum rules.
4. A 45-day suspension will be issued if the user is found to be a habitual rule breaker.
5. Habitual rule breakers that have exhausted all of the above will receive a permanent life-time ban that will be strictly enforced. Reinstatement will not be allowed – there is no appeal process.

Subsequent accounts created in an effort to side-step the rules and moderation process are subject to automatic removal without notice. Firehouse.com reserves the right to expedite the reprimand process for any users as it is deemed necessary. Any user in the moderation process may be required to review and agree to by email the terms and conditions listed above before their account is re-instated (except for those that are banned).

Firehouse.com reserves the right to edit and/or remove any post or member, at any time, for any reason without notice. Firehouse.com also reserves the right to warn, suspend, and/or ban, any member, at any time, for any reason.

Firehouse.com values the active participation we have in our forums. Please ensure your posts are tasteful and tactful. Thank you very much for your cooperation.
See more
See less

Room Occupancy Formula?

Collapse
X
 
  • Filter
  • Time
  • Show
Clear All
new posts

  • Room Occupancy Formula?

    Is there a set standard or formula for determining room occupancy? [I live in the USA.] I realize that perhaps each jurisdiction is free to set their own standards but I'm wondering about a national code. I've done a search online and found some varying results. I'd like to be able to point to something official or as close as I can get.

    The buildings I have in mind are commercial, no more than 4 stories tall, and a mix of conference rooms, auditorium, labs, and workshops. This is an exercise for my own purpose and will not be used in any official way.

    Here's hoping someone can link me or post some guidelines here.

    Thanks!

    - Keen

  • #2
    The International Fire Code sets occupancy levels dependent on the type of occupancy, class of construction, whether the building is sprinklered or not, number of fire exits, and other factors. I would suggest getting a copy of the IFC through the International Code Council.
    "Loyalty Above all Else. Except Honor."

    Comment


    • #3
      check table 1004.1.2


      http://academics.triton.edu/faculty/...from%20IBC.pdf


      you have to know the square footage of the floor/ building

      the use of each room/ area

      then pick out the closest thing on the table and divide by the factor.
      that will give you rough estimate

      such as office use with 3000 sq ft/ 100 = 30 occupants.
      http://www.youtube.com/watch?v=JZdEH...e_gdata_player

      Comment


      • #4
        what state are you in?

        and possibly city if you want to post it???
        http://www.youtube.com/watch?v=JZdEH...e_gdata_player

        Comment


        • #5
          Thanks for the replies. It's helped.

          Originally posted by fire49 View Post
          what state are you in?

          and possibly city if you want to post it???
          Virginia, Loudoun County (west of DC)

          Comment


          • #6
            Your state has a "state" code which cannot be changed locally


            """"The local code officials and inspectors must enforce the USBC as adopted by the board, without authority to make any amendments.* The purpose of this system of adoption and enforcement is to benefit the citizens of Virginia by promoting uniformity and efficiency in the construction industry, many aspects of which are interstate in nature.""""



            http://www.dhcd.virginia.gov/StateBu...lding_Code.htm
            http://www.youtube.com/watch?v=JZdEH...e_gdata_player

            Comment


            • #7
              Also a lot depends on regional differences.

              Say for example, a 20x20 room might be able to accommodate 80 women from Texas. The same room will fit 30 women from Ohio or 10 women from Nebraska.
              ~Drew
              Firefighter/EMT/Technical Rescue
              USAR TF Rescue Specialist

              Comment


              • #8
                The Life Safety Code, NFPA 101 has a table for determining occupancy loads based on a few factors. Using a number of square feet per person, it takes the size of the given space and returns the number of people the space can safely hold. The OL then determines what safety features are necessary, rather than modifying the OL to what features are there. Clear as mud? Basically the actual size and use of the space determines the number of people allowed, then based on the number they determine how you must protect the occupants. This way you do not rely on the building owners/occupants to regulate occupancy numbers, but in fact protect them anticipating the "worst case".

                Thus your answer depends on what code the occupant load calculations are based in in your State.

                Comment


                • #9
                  Originally posted by FiremanLyman View Post
                  Also a lot depends on regional differences.

                  Say for example, a 20x20 room might be able to accommodate 80 women from Texas. The same room will fit 30 women from Ohio or 10 women from Nebraska.
                  I thought everything was bigger in Texas! You guys really need to get a handle on the meth problem down there!

                  Comment


                  • #10
                    Don't forget - in addition to the square footage calculations, you need to take into account the number of EXITS, their orientation (if there is more than one) - and their size!......

                    A room with only 1 exit, no matter the size, is limited to 50 people.

                    For a room with multiple exits that are REMOTE from each other, generally you calculate .2 inches per person in the exiting capacity - for an unsprinklered building.

                    Comment