Leader

Collapse

Announcement

Collapse

Firehouse.com Forum Rules & Guidelines

Forum Rules & Guidelines

Not Permitted or Tolerated:
• Advertising and/or links of commercial, for-profit websites, products, and/or services is not permitted. If you have a need to advertise on Firehouse.com please contact [email protected]
• Fighting/arguing
• Cyber-bullying
• Swearing
• Name-calling and/or personal attacks
• Spamming
• Typing in all CAPS
• “l33t speak” - Substituting characters for letters in an effort to represent a word or phrase. (example: M*****ive)
• Distribution of another person’s personal information, regardless of whether or not said information is public knowledge and whether or not an individual has permission to post said personal information
• Piracy advocation of any kind
• Racist, sexual, hate type defamatory, religious, political, or sexual commentary.
• Multiple forum accounts

Forum Posting Guidelines:

Posts must be on-topic, non-disruptive and relevant to the firefighting community. Post only in a mature and responsible way that contributes to the discussion at hand. Posting relevant information, helpful suggestions and/or constructive criticism is a great way to contribute to the community.

Post in the correct forum and have clear titles for your threads.

Please post in English or provide a translation.

There are moderators and admins who handle these forums with care, do not resort to self-help, instead please utilize the reporting option. Be mature and responsible for yourself and your posts. If you are offended by another member utilize the reporting option. All reported posts will be addressed and dealt with as deemed appropriate by Firehouse.com staff.

Firehouse.com Moderation Process:
Effective immediately, the following moderation process will take effect. User(s) whose posts are determined by Firehouse.com staff to be in violation of any of the rules above will EARN the following reprimand(s) in the moderation process:
1. An initial warning will be issued.
2. A Final Warning will be issued if a user is found to be in violation a second time.
3. A 3-day suspension will be issued if the user continues to break the forum rules.
4. A 45-day suspension will be issued if the user is found to be a habitual rule breaker.
5. Habitual rule breakers that have exhausted all of the above will receive a permanent life-time ban that will be strictly enforced. Reinstatement will not be allowed – there is no appeal process.

Subsequent accounts created in an effort to side-step the rules and moderation process are subject to automatic removal without notice. Firehouse.com reserves the right to expedite the reprimand process for any users as it is deemed necessary. Any user in the moderation process may be required to review and agree to by email the terms and conditions listed above before their account is re-instated (except for those that are banned).

Firehouse.com reserves the right to edit and/or remove any post or member, at any time, for any reason without notice. Firehouse.com also reserves the right to warn, suspend, and/or ban, any member, at any time, for any reason.

Firehouse.com values the active participation we have in our forums. Please ensure your posts are tasteful and tactful. Thank you very much for your cooperation.
See more
See less

Emergency Lighting

Collapse
X
 
  • Filter
  • Time
  • Show
Clear All
new posts

  • GPM1230
    replied
    UPDATE.
    This is one large open space with a kitchen on one end. We approved photoluminescent door frame markings in addition to the Exit signage. The markings to be a minimum 1" wide.

    Leave a comment:


  • GPM1230
    replied
    dhavenshome.
    You have captured the issue very well. Not only scouts using the place. Also, I work for the AHJ I have approved the photoluminescent exit signs. I will keep working with them for a solution. I have a couple of things in mind. Will let you know what we approve. Thanks

    Leave a comment:


  • nt8d09
    replied
    I am presuming this is a fixed structure, such as a log cabin of sorts that is enclosed or semi-enclosed.

    If the AHJ requires you to have emergency lights, and you can't find any middle ground. Perhaps consider an emergency light setup with a central battery, so you only need to replace one or two big batteries, instead of a bunch of independent heads with their own batteries.

    Leave a comment:


  • CJFor
    replied
    Could you use photoluminescent or radioluminescent exit signs?

    Leave a comment:


  • dhavenshome
    replied
    Unique problem. Clearly requires discussion with the local AHJ. While the generator will keep the backup batteries charged during use, the life of batteries when the not connected to a power source is limited by the type of battery and the environment where the are located. Heat and cold in particular...similar to what happens with a car battery when the car is not run for a long time. In this case, when the generator is turned off, the emergency lights come on and will drain the battery(ies) until the have no charge. In this state, the batteries may not take a charge the next time the generator is run, and even if they do, they wouldn't be in the fully charged state, necessary to meet the 90 minutes standby, for hours. The good news is that with LED lighting, the batteries required have become a lot smaller. Although it requires some work, bringing enough fully charged batteries with you and installing them before the event.

    As a longtime scouter, this issue could be resolved if the local AHJ was able to accept a requirement that the Scouts carry their flashlights with them (which they already do to navigate from their camps to the assembly hall at night).

    Leave a comment:


  • fire49
    replied
    Highly suggest post the question here:::


    https://www.thebuildingcodeforum.com...cal-codes.116/


    Leave a comment:


  • fire49
    replied
    I would say since already running off a generator, use it,

    Plus emergency lights with battery back up.

    Seem like the only time the place should be in use, is when the generator is running.

    So when the gen runs, the batteries are recharged.

    Other than that solar system with battery group, for back up.

    Leave a comment:


  • GPM1230
    started a topic Emergency Lighting

    Emergency Lighting

    An assembly occupancy that only runs on generated power when in use. No power to the building otherwise. (Remote Scout camp) Looking for suggestions for emergency lighting. With the normal ones the battery goes dead because of the long time without power between events.

    Thanks