Not bragging but I would be willing to bet there are few who have spent as much time and effort to find effective ways to use the Turbo Draft as I have. I'm not selling it, just saying that if you think outside the box a little you can greatly improve your usable water numbers from where they are now. What would be your reaction to going from 5 to 600 gallons per minute to getting 1100 gallons per minute. Or what would you think of having three (3) engines all drafting from one (1) drop tank with a combined flow of approximately 3000 gallons per minute all being supplied by Turbo Draft. I've run 400 feet of 5inch from the turbo, connected it to the engine and still turned 500 gallons per minute. It's not a single method use tool. The ways to use it are many. I have pictures and documentation of these efforts, enough to where the use of this device is taught in our Basic Pump Operations and Rural Water Supply classes. But then we also do weird things like combine the efforts of three (3) portable pumps to achieve flows of 1000 gallons per minute. I'm not advertising but the Albemarle County Spring schedule is getting ready to start. If you have any questions feel free to look us up and drop me a line.
Dale Deane
IAFF Local 4077
Albemarle County Fire Rescue
Albemarle County Virginia
Leader
Collapse
Announcement
Collapse
No announcement yet.
How far horizontally can you draft from a source?
Collapse
X
-
Originally posted by txgp17 View PostThis is one of the hardest "inside the box" ideas to get away from. Why do we buy HSH in 10' sections? Because that's the way we've always done it? Because that's what is required for the cert/accept/service tests?
If you have a 12' body, why not have 12' sections of HSH? If you have a ladder rack holding a 14' ladder, why not have it hold 14' sections of HSH?
On most rigs there is adequate room to stack them two high on each side of the hosebed. Imagine if every truck in your inventory carried four 14' sections and a floating dock strainer. That makes at lot more bodies of water useful water points.
Here is a setup we did at a recent pump classes.
This was a 50' draft. We filled tankers at about 1000 GPM. We never did test the actual flow capability of the configuration, to my dismay.
Looking down from on top of the rig.
This configuration was 60 feet, and in water about 10 inches deep at best. We used a rock to weigh the low level strainer down. The point we were trying to illustrate was twofold-One---you can use more suction hose than your rig carries. Two---you can draft in crappy sources as a last resort.
Another view.
This was tested and we were able to acheive 500 GPM. The pump was rated 1750. Certainly not ideal, but usable in a pinch.Last edited by MG3610; 09-03-2010, 11:42 AM.
Leave a comment:
-
Originally posted by txgp17 View PostThis is one of the hardest "inside the box" ideas to get away from. Why do we buy HSH in 10' sections? Because that's the way we've always done it? Because that's what is required for the cert/accept/service tests?
If you have a 12' body, why not have 12' sections of HSH? If you have a ladder rack holding a 14' ladder, why not have it hold 14' sections of HSH?
On most rigs there is adequate room to stack them two high on each side of the hosebed. Imagine if every truck in your inventory carried four 14' sections and a floating dock strainer. That makes at lot more bodies of water useful water points.
I thinks I likes it...
We have a double on one truck... E-One was kind enough to stack em so tight that you can't slide the bottom section of suction out the rear because the couplings catch(Gotta have two tall fellows to pull em off the side.) Yes, it is a spec error on our part...but I gotta blame someone.
Leave a comment:
-
Originally posted by neiowa View PostKochek will make up in whatever length you want (no requirement to be 10').
If you have a 12' body, why not have 12' sections of HSH? If you have a ladder rack holding a 14' ladder, why not have it hold 14' sections of HSH?
On most rigs there is adequate room to stack them two high on each side of the hosebed. Imagine if every truck in your inventory carried four 14' sections and a floating dock strainer. That makes at lot more bodies of water useful water points.Last edited by txgp17; 08-19-2010, 12:11 AM.
Leave a comment:
-
Originally posted by WBFD25 View PostThe problem with setting a dump tank up behind the primary pumper is not many pumpers are equipped with an intake on the rear of the vehicle. That is why it works best to put it either directly on the side, the best route, or out front off a front suction intake on the bumper. Not to mention the amount of hard suction you'd require to bend off the side intake, or front even, to get the suction hose back to a drop tank set up behind a standard pumper.
Placing the tank in front of the engine works well in that the pump operator can easily check on the status of available water, plus if shorthanded, its allows him to direct the tanker/tender driver into place without having to walk all around the engine.
More often than not, the drivers get short-sighted and pull right up into the driveway instead of backing in. If they took the extra 30-45 seconds to back in, putting a drop tank up front would be the best solution. Instead, they get tunnel vision and go in nose-first. Then you get stuck performing nursing operations, which as pointed out, are slow and more labor intensive.
Or buy one (1) section of hard suction length required. Kochek will make up in whatever length you want (no requirement to be 10').
Leave a comment:
-
Originally posted by islandfire03 View PostWe have many long narrow rural driveways with many of them 1/2 mile or more in length from the road, We try to have the attack engine drop the 4 inch ldh and rural hitch at the end on the way into the scene.
All engines carry 1250 ft of 4" so it might take the hose lay off two engines to complete the supply set up,on the longer drives. The second in engine will have the tankers set up their porta tans across the end of the drive after they pull in to the end and hook up to the ldh. that way all the tankers have to do is pull up and side dump on the way by.
We use up to 30 feet of hard suction to feed the supply engine from the porta-tanks. We use a water witch to feed additional tanks into the primary tank so the tanker operator can drop their entire load and get back on the road to the water source.
this seem to eliminate backing into long drives or trying to get turned around to exit.
Leave a comment:
-
We have many long narrow rural driveways with many of them 1/2 mile or more in length from the road, We try to have the attack engine drop the 4 inch ldh and rural hitch at the end on the way into the scene.
All engines carry 1250 ft of 4" so it might take the hose lay off two engines to complete the supply set up,on the longer drives. The second in engine will have the tankers set up their porta tans across the end of the drive after they pull in to the end and hook up to the ldh. that way all the tankers have to do is pull up and side dump on the way by.
We use up to 30 feet of hard suction to feed the supply engine from the porta-tanks. We use a water witch to feed additional tanks into the primary tank so the tanker operator can drop their entire load and get back on the road to the water source.
this seem to eliminate backing into long drives or trying to get turned around to exit.
Leave a comment:
-
Originally posted by WBFD25 View PostPlacing the tank in front of the engine works well in that the pump operator can easily check on the status of available water, plus if shorthanded, its allows him to direct the tanker/tender driver into place without having to walk all around the engine.
More often than not, the drivers get short-sighted and pull right up into the driveway instead of backing in. If they took the extra 30-45 seconds to back in, putting a drop tank up front would be the best solution. Instead, they get tunnel vision and go in nose-first. Then you get stuck .
The hypothesis at this point is to place the pond at the end of a drive (country setting) across the first lane of traffic. The idea is that a tanker(tender) can drive to the side of the pond and side dump or pull past and then back in and rear dump.
Leave a comment:
-
Originally posted by volfireman034 View PostThere are times when setting up the dump tank several feet behind the pumper would work much better for a tanker (tender) to drop their load, but most departments around here insist on dump tank 3 feet in front of pump panel or nothing. When I use the term nurse tanker, for us, that means a tanker pulls up near the pumper and we pull ( or push if tanker has a pump) the water directly from the tanker to the pumpers intake. Problem is when the tanker is empty you have to disconnect everything move that tanker out of the way then move the next tanker in place and rehook. All of which takes way to much time.
Placing the tank in front of the engine works well in that the pump operator can easily check on the status of available water, plus if shorthanded, its allows him to direct the tanker/tender driver into place without having to walk all around the engine.
More often than not, the drivers get short-sighted and pull right up into the driveway instead of backing in. If they took the extra 30-45 seconds to back in, putting a drop tank up front would be the best solution. Instead, they get tunnel vision and go in nose-first. Then you get stuck performing nursing operations, which as pointed out, are slow and more labor intensive.
Leave a comment:
-
There are times when setting up the dump tank several feet behind the pumper would work much better for a tanker (tender) to drop their load, but most departments around here insist on dump tank 3 feet in front of pump panel or nothing. When I use the term nurse tanker, for us, that means a tanker pulls up near the pumper and we pull ( or push if tanker has a pump) the water directly from the tanker to the pumpers intake. Problem is when the tanker is empty you have to disconnect everything move that tanker out of the way then move the next tanker in place and rehook. All of which takes way to much time.
Leave a comment:
-
FM
We use 10, 20, or 30 feet with a porta tank. It just depends on tank placement and the surrounding. Of course less is better because of set up times and less chance of air leaks.
Leave a comment:
-
Originally posted by volfireman034Wow glad I read this I was always told drafting more the 20 ft from any water source was about the limit didn't matter if it is was horizontal or virtical. So I guess I can start moving my dump tank alittle further way from the pumper ( assuming theres room) to give us more room to work around the pumper and get tools? Most firefighter around here insist the dump tank be right next to the pump panel or that won't use it and that use the nurse tanker set up which for me is 100 times harder and not as effective.
Drafting horizontally and vertically are 2 different operations with 2 different results. Same with length of the hard line you are trying to draft with.
You lost me on the last comment. Hooked on phonics???
FM1
Leave a comment:
-
Wow glad I read this I was always told drafting more the 20 ft from any water source was about the limit didn't matter if it is was horizontal or virtical. So I guess I can start moving my dump tank alittle further way from the pumper ( assuming theres room) to give us more room to work around the pumper and get tools? Most firefighter around here insist the dump tank be right next to the pump panel or that won't use it and that use the nurse tanker set up which for me is 100 times harder and not as effective.
Leave a comment:
-
Originally posted by Stuart View PostTry installing a dry hydrant.
Lower friction loss (with properly sized piping)
.
Leave a comment:
-
NEIOWA: Expect to reduce your flow by about 100 gpm for every 10' joint of hard sleeve you add beyond 20 feet. For a 1500 gpm pump with 60' of hard sleeve you should get about 1100 gpm at a 10' lift. Be very careful as you throttle up. It will be easy to cavitate at high flow rates. Like others on here have said, "expect to have some long priming times." For pumps larger than 1500 GPM you need suction from two intakes to meet the pump spec. so with only one 6" sleeve, expect to see no difference between a 1500, 1750, or 2,000 gpm engines.
Leave a comment: