View Full Version : Foam Question?


Spencer534
04-27-2005, 05:51 PM
Is there anyone who can direct me to info or knows themselves about AFFF foam on class A fires. My co-workers say there are tremendous benefits on class A and car fires. I say there is not, however, a salesman showed them some dog and pony show using a piece of cardboard and spraying it with AFFF. Any help would be appreciated.

lvwrench
04-27-2005, 06:06 PM
Don't really know if this will help but we have had dual foam systems, A&B in sperate tanks on our units for some time. The time has finally come to say NO to carrying two kinds of foam. The trouble is that if you accidentally mix foams there is a tendency for coagulation(the stuff turns to a gel)and won't properly dispense if at all. If you crank up the percentage on Class A foam it works just fine in lieu of Class B.

Dave1983
04-27-2005, 06:17 PM
Im not a foam expert, but I dont belive that imformation to be accurate.

Each type of foam works in a different way. Class "A" breaks down the surface tension of the material which allows water to be more effective. Class "B" works to smother the fire.

While I can see how class "A" may work with certain class "B" materials, I dont think it would be effective for others. Take a fuel spill, with or without fire. You need the class "B" to smother the fire or to "coat" the spill to prevent ignition. If you applied class "A" , all you would do is spread the spill and do little, if anything, to prevent an ignition.

We have had multiple agent tanks for years, and will continue to do so. Each type of foam has its "place" and dropping one will only limit your options and capabilities.

Berks2Montco84
04-27-2005, 06:40 PM
Actually Dave, I belive Class A foam breaks down the surface tension of the WATER, not the actual material, but you were close. :D

Station2Capt
04-27-2005, 06:41 PM
Dave is correct with his post. Class A foam and Class B foam are two different products with two different uses. Class A foam is not sutiable on liquid hydorcarbon spills because it lacks the Film Forming action (2 of the F's in AFFF) found in Class B foam. There are too many things about foam to discuss here. If you want to learn more about foam to www.usfoam.com (http://www.usfoam.com) I know the owner of this company and if you dont find what you need just drop him an email he loves to talk foam and would help out anyone.

hvfd507
04-27-2005, 10:13 PM
If you think about what is actually burning in most car fires, "A" class foam may be the right call. Rubber, cloth, vinyl, and plastics are easily handled with the "A" class. Its very rare we are dealing with flammable liquids with car fires, around here anyway. Just a thought. Also, we have a/b foam on our units. Never had trouble keeping them apart.

Rescue101
04-28-2005, 09:57 AM
I'm Confused.Foam rubber,plastic,fibreglass etc are CLASS B MATERIALS.Therefore they are B foam.Class A is for A materials(THAT LEAVE AN ASH).Not much in a vehicle fire fall in that category.Will Class A "work"on a car fire? Yes,but that's not what it was specfically designed for. T.C.

Dave404
04-28-2005, 11:44 AM
This may help - just grabbed it off the website.

CHEMGUARD CLASS A PLUS FOAM
Chemguard's Class A foam concentrate is a mixture of foaming and wetting agents. When proportioned with water it changes the properties of the water, reducing the surface tension and allowing for greater penetration in all Class A fuel and wild land fires. It also gives the water a foaming ability allowing it to remain and cling to the surfaces without run off. Class A is effective in fighting forest fires and many deep-seated fires such as tires, paper, and wooden structures.

-Chemguard's Class A Plus is a noncorrosive, non-toxic biodegradable Class A fire fighting foam concentrate and is suitable for use through medium expansion discharge devices, compressed air foam systems (CAFS) and arial bambi buckets
-Recommended application rates from 0.1% to 1.0%. Class A Plus is manufactured, tested and evaluated in accordance with NFPA 298, specifications for Class A foams for wild land fires, helicopter bucket operations, and ground applications
-Benefits: 3 to 5 times more effective than plain water
-Can be used with either fresh or salt water
-Can be used with non-air-aspirating or aspirating handline nozzles
-Suitable for use on rubber (tires), coal, paper and many other types of Class A fuels

(CLASS B, 3% OR 6% SYNTHETIC AFFF FOAM)
Application of AFFF provides the fastest knockdown on hydrocarbon fuel fires (gasoline, kerosene, diesel, etc.) and quickly covers the fuel surface.

-AFFF may also be used on Class A fires
-Biodegradable and environmentally friendly
-Suitable for use with both fresh or salt water
-Suitable for use with all siliconized dry chemical agents
-Suitable for use with air-aspirating and standard water fog nozzles
-Suitable for use with the following types of proportioning equipment: Fixed or in-line eductors, in-line balanced pressure and pump pressure proportioning skid, bladder tank balanced pressure proportioning system, and handline air-aspirating nozzles with fixed eductor pickup tube
-Suitable for use with the following discharge devices: Foam chambers, air-aspirating and non air-aspirating sprinkler heads or spray nozzles, standard water fog nozzles for handlines and monitors, air-aspirating foam nozzles, foam makers for use with either floating roof storage tanks or dike/bund protection systems, and high back pressure foam makers for sub-surface base injection system (hydrocarbon type fuel only)
-Will provide quality protection in areas such as: Crash fire rescue, storage tanks (non-polar solvent type fuels only), truck/rail loading or unloading facilities, processing/storage facilities, docks/marine tankers, flammable liquid containment areas and mobile equipment

Fawlty
04-28-2005, 12:37 PM
I'm Confused.Foam rubber,plastic,fibreglass etc are CLASS B MATERIALS.Therefore they are B foam

Errrr.... actually, Rubber, plastic etc. are actually class 'A' materials. I understand that your belief perhaps comes from the high quantity of hydrocarbons present in the product, but as a solid they are considered a class 'A' product. Class 'B' products are Flammable Liquids, e.g. gasoline, kerosene, oil etc.

A car fire, unless your dealing with a ruptured fuel tank with resulting spill, is a class 'A' fire, and is very effectively extinguished with a class 'A' foam, whether it be Air Aspirated or compressed Air generated, or even a wet water solution, class 'A' concentrate mixed with water. With the size of most car fuel tanks even the burning class 'B' product is easily extinguished with a class 'A' foam.

Fuel spills of any appreciable size are best dealt with by using a class 'B' foam with film forming properties (not all 'B' foams form film (try saying that three times fast)). However, if your department is equipped with only class 'A' foam, a blanket of 'dry'(if you are using CAFS) foam can be applied to prevent vapor formation and assist in isolating the fuel from an ignition source. However, provided you understand that the hydrocarbon fuel will cause class 'A' foam to break down more rapidly than under normal circumstances, and that it does not provide any protection for gaps in the foam blanket.

I've had the experience to work with many foams, and with the exception of alcohols, it's suprising how well you can use one foam for a multitude of different problems.. provided you know their limitations.

DennisTheMenace
04-28-2005, 12:40 PM
Originally posted by Fawlty


Errrr.... actually, Rubber, plastic etc. are actually class 'A' materials. I understand that your belief perhaps comes from the high quantity of hydrocarbons present in the product, but as a solid they are considered a class 'A' product. Class 'B' products are Flammable Liquids, e.g. gasoline, kerosene, oil etc.

A car fire, unless your dealing with a ruptured fuel tank with resulting spill, is a class 'A' fire, and is very effectively extinguished with a class 'A' foam, whether it be Air Aspirated or compressed Air generated, or even a wet water solution, class 'A' concentrate mixed with water. With the size of most car fuel tanks even the burning class 'B' product is easily extinguished with a class 'A' foam.

Fuel spills of any appreciable size are best dealt with by using a class 'B' foam with film forming properties (not all 'B' foams form film (try saying that three times fast)). However, if your department is equipped with only class 'A' foam, a blanket of 'dry'(if you are using CAFS) foam can be applied to prevent vapor formation and assist in isolating the fuel from an ignition source. However, provided you understand that the hydrocarbon fuel will cause class 'A' foam to break down more rapidly than under normal circumstances, and that it does not provide any protection for gaps in the foam blanket.

I've had the experience to work with many foams, and with the exception of alcohols, it's suprising how well you can use one foam for a multitude of different problems.. provided you know their limitations. yep

CaptOldTimer
04-29-2005, 12:43 PM
Originally posted by Spencer534
Is there anyone who can direct me to info or knows themselves about AFFF foam on class A fires. My co-workers say there are tremendous benefits on class A and car fires. I say there is not, however, a salesman showed them some dog and pony show using a piece of cardboard and spraying it with AFFF. Any help would be appreciated.


From your posted location by looking on the atlas, why don't you check with the guys in the bigger departments West of your location and see what they are using. I would also think the since there ia a major airport near you, that they and maybe the Air Guard, if one is there, may be using what you are looking for.

Just a suggestion.

Resq14
04-29-2005, 02:03 PM
.

AC1503
04-30-2005, 02:35 AM
We are considering giving F-500 a try. It is not an actual foam, but is rated for both class A and B fires. Does anyone have any experience with using it? Also comments on its effectiveness are requested. We would like to know both sides of the story, anything good or anything bad.

5pts384
04-30-2005, 11:55 AM
We have class A foam on our brush truck, we have found that it will put out a (fat lighter) house much better than water. Our 30+ year old trucks are not equiped with foam:(

PattyV
04-30-2005, 12:03 PM
It isnt very hard to set up a foam system, im not an expert on it, but we jost got a new truck and our first officer put the foam proportionng system on and set up the hoses in about an hour.
(took him about 6 weeks to get around to actually doing it though)
Surely it cant be too much hassle for you guys to put one on.

Frosty42
04-30-2005, 12:12 PM
We had both class A & B foam tanks on three of our engines, but changed them all to Class A. I have used class A on many car fires in the last three years and it is not a solve all extinguishing agent. But, faced with a fully involved auto, class A works very nice. Even better when you have exposures. It will buy you some time.
For structure fires though...still very effective and my first choice. But I have noticed that the compartment is much hotter, especially when using compressed air foam systems.

Fawlty
04-30-2005, 12:24 PM
For structure fires though...still very effective and my first choice. But I have noticed that the compartment is much hotter, especially when using compressed air foam systems.

Absolutely, there is considerably less water in a CAFS line and subsequently less water in the fire compartment. That can be good of course to help minimize water and run off damage, lighten hose lines etc... I was always instructed to keep a CAFS line flowing after the fire is extinguished for about an equal time that it took to achieve knockdown. This assists in cooling and prevents rekindle.

Personally I like working with CAFS.. makes a little water go longer (yeah yeah, I know, for a big fire, you still need big water!!) :D

Cheers

Spencer534
04-30-2005, 04:23 PM
I don't think I explained myself with my original question. I have never used foam except in these two situations: AFFF on fuel spills/fires and Class A on brush fires. The 2 guys I am on shift with swear by using AFFF on car and structure fires. I have found that water (when applied correctly) works fine on those calls and have never needed to use foam, nor since working with them have I seen a difference when it was used. The larger departments around me (including the Air Guard) use foam in the same way I have been taught. I don't want to miss out on a good thing if AFFF should be used. One co-worker even wants to put AFFF in the water can. I have heard of separate cans with AFFF for oil furnace/Class B fires, but not for structure fires. Are there firefighters who are using AFFF for structure/car fires and if so, can you explain the science behind it and is it cost effective (water is cheap and plentiful!)?

Dave1983
05-01-2005, 12:16 AM
Originally posted by Spencer534
I don't think I explained myself with my original question. I have never used foam except in these two situations: AFFF on fuel spills/fires and Class A on brush fires. The 2 guys I am on shift with swear by using AFFF on car and structure fires. I have found that water (when applied correctly) works fine on those calls and have never needed to use foam, nor since working with them have I seen a difference when it was used. The larger departments around me (including the Air Guard) use foam in the same way I have been taught. I don't want to miss out on a good thing if AFFF should be used. One co-worker even wants to put AFFF in the water can. I have heard of separate cans with AFFF for oil furnace/Class B fires, but not for structure fires. Are there firefighters who are using AFFF for structure/car fires and if so, can you explain the science behind it and is it cost effective (water is cheap and plentiful!)?

For the situations you mentioned (car & structure) you CAN use both types of foam. Its up to your department and what they feel works best. For us, a structure would get class "A", a car class "B".

Yes, water works, its just that foam works better. This realy comes into play with class "A" on structure fires. The foam makes the water more effective. The fire goes out faster and you use less water. If you ever use it, you will see what I mean.

We used to put AFFF in our water cans, now we put class "A".

As for rubber/plastic being a class"A" material, yes and no. In its solid, unburned form it is. But when it burns and melts, its degradeing and returning to its original "form". Thats why we use AFFF on car and fiberglass boat fires;)

ullrichk
05-01-2005, 04:10 AM
The AFFF we use is suitable for class A fires at low percentages (says so on the instructions). The foam acts as a wetting agent, breaking down the surface tension of the water, allowing it to penetrate better and put the fire out quicker. Not surprisingly it also works well at 3% and 6% for class B fires - since that's what it is primarily used for. (For anyone who doesn't know, big drops of water don't penetrate class A materials like baled hay or fabric particularly well. Reducing the surface tension allows the water to flow into the pores and voids instead of beading up and rolling off.)

If you want to know if you should use it at every fire you also need to look at things like cost, how the concentrate acts when open to air for long periods of time, how corrosive the concentrate is to your pump and piping, and whether or not it will gum up the works if you don't get it all flushed out.

My department also use F-500. Keep in mind that F-500 is an emulsifier that also acts as a wetting agent - there's no magic going on here. I've posted about it several times (do a search and you'll find some examples).

stillPSFB
05-01-2005, 08:25 AM
We don't carry the traditional water can on any of our apparatus, so I'm wondering how well an AFFF extinguisher would work as a water can for the traditional ladder company Canman on a search team working without a hoseline?

captstanm1
05-01-2005, 10:12 AM
I belive Class A foam breaks down the surface tension of the WATER, not the actual material, but you were close.

That is correct....

As far as the original question:Is there anyone who can direct me to info or knows themselves about AFFF foam on class A fires.It depends on the type of foam system you have. Is it effective? Yes....It can be. However, unless you have a proportioner that will proportion you Class B Foam down to .5% or lower, you are using a very expensive foam to combat class A fires. Most foam systems unless it is the Hale FoamLogix will not proportion both Class A and B Foams...

FoamLogix 3.3 and 5.0
The Hale FoamLogix handles Class A and most Class B foams, as well as high viscosity alcohol resistant foams made for application on polar solvents.

Foam electronics feature advanced microprocessor technology with simple push-button operation, system capacity monitoring, continuous operation regardless of the pump suction and discharge PSI.

The FoamLogix has electronic discharge side foam proportioning and rotary gear technology to give you the benefit of using most Class B dual purpose foam concentrates manufactured for both normal hydrocarbons and polar solvents

Your traditional systems (in line eductors and behind the pump panel)are designed to flow 1% to 6%. With the foamlogix you can dial in the lower amount. However, when you attempt to cut the class b foams...(even low viscosity) they tend to lose their effectiveness somewhat. This is especially true in the Foam Pro system which has a very hard time proportioning Class B as it is designed specifically for Class A.

A lot of folks use traditional nozzles and class B foam for auto fires. Others in this area carry class A foam in their on board tanks and use it for everything. It extends your water capabilities and is very effective on Auto Fires. If their system is a Class B system they flow it at 1%. If they have the FoamLogix system they they dial it down to .1% or .5% and use it as a wetting agent. Class A Foam is not effective for blanketing spills or combatting Class B Flammable and Combustible liguid fires. While at 6% (in some foams) it will appear to give you a very thick homogenous blanket, there is no membrane to suppress vapors. So while it may assist in extinguishing the fire, it will provide no protection against re-ignition of vapors.

For more information I suggest you contact Jim Cottrell of Cottrell & Associates. jimcott@aol.com He is the most knowledgable person I have ever met on the subject of foam. He has significant research papers and information on this subject that he will gladly share with you. He is the Foam Rep for National Foam.

5pts384
05-01-2005, 11:08 AM
From what I have read, class B foam only works on standing fuel (puddled). If the fuel is moving it can't make a film over the fuel.

Fawlty
05-01-2005, 12:48 PM
Class A Foam is not effective for blanketing spills or combatting Class B Flammable and Combustible liguid fires. While at 6% (in some foams) it will appear to give you a very thick homogenous blanket, there is no membrane to suppress vapors. So while it may assist in extinguishing the fire, it will provide no protection against re-ignition of vapors.

As I said in an earlier post, while Class A foam absolutely does not provide the same protection offered by Class B Film Forming Foams (again not all class B's are film forming), a thick dry layer of Class A CAFS will provide limited protection when used on a fuel spill. It will suppress vapors for as long as the foam blanket remains intact, and will isolate the fuel somewhat from an ignition source. In other words, as a responding company faced with a medium, non-flowing spill, and one with no stocks of Class 'B' PFFF or AFFF, then you may want to set your CAFS to a nice dry setting and place a layer of foam on the fuel. This will give you at least a limited protection until you can resolve the situation completely.

Work with what you've got. We no longer carry Class B concentrate, and have to use what resources we have. If you have any doubt about the vapor suppressing abilities of an intact blanket of CAFS on a Class 1 class B liquid, try putting an inch or two of gasoline in a burning tray (like for extinguisher training), CAFS it up and start throwing matches (safely of course). Let me know how many books you go through!! :rolleyes:

LaFireEducator
05-01-2005, 09:27 PM
I have also been taught that Class A can be used as an initial attack line on a Class B fire. While it will not keep the vapors supressed, and can be used in fire attack if Class B foam is not available, and will cool the spill if it is applied liberally until Class B can be applied. In terms of thwe Class B foam on a Class A fire ..I have no experience with that, but I do know at the cost of class B foam, as compared to class A, I sure can't see my department doing that.

fdmhbozz
05-01-2005, 09:52 PM
We use FireAde 2000, which is a Class A and Class B foam.

Rescue101
05-02-2005, 09:22 AM
Stan,I beg to differ with you in regards to the Foam pro.We have a A/B 2001 model on our primary Engine and from what I can see it applies EITHER A or B with equal efficiency. Fawlty,As far as the Class A/B question,I was always taught if the burning material leaves an ASH it is Class A,if not it is B(or C or D).Now burning tires DON'T leave much ash.Neither does foam rubber,plastic,or fiberglass.Oh,fiberglass will leave the cloth backing residue but that not really ash either.And we can argue the point 'til the cows come home,but in the end result it will depend on whose product you use and how you apply it how effective it is.Since I have both,it's merely a flip of the wrist to change product if it's application is not effective.As you travel the country you'll find that different people have widely ranging opinions on this subject.Do your homework and find out what works for You,T.C.

Resq14
05-02-2005, 09:52 AM
Most of the sources I've seen consider products like tires and insulation to be Class A fires. Most foam companies consider them Class A.

You're going to have a tough time forming a vapor film over such materials, so why bother blowing through Class B foam at a 10x-20x rate?

If Fireade were cheaper, and if it performed better in a CAF system, I wouldn't mind switching to it. But we have had better results with Class A foam in our CAFS. Fireade is not a foam, and as a result it does not work well.

For the usual fuel leaks and fuel fires we have (small ones), an APW with some AFFF works just as well. We did side-by-side tests, and the APW with AFFF extinguished Class B fires much faster. Don't get me wrong, Fireade does have some benefits (emulsification properties, product stability, etc). I just don't feel they outweigh the cons at this time, given our equipment and jurisdiction.

Fawlty
05-02-2005, 12:25 PM
Rescue101.. This reply is by no means an attempt to bust your chops, but purely to provide a standard for classifications of fires. I absolutely understand that what you are taught by an instructor can leave a long and lasting impression, but sometimes, not every time, in fact not even most times, an instructor can oversimplify something to make it easier for students to understand.

Rubber, fiberglass etc.. is not a Class 'B' fire, it is Class 'A', (cows coming home or not). In its normal state, it is a solid. Burning rubber may drip, and occasionally pool with moderate movement, but once cooled with a water jet, will return to a solid state. You can, and I have on many occasions, extinguish a rubber fire with a Class 'A' (water) extinguisher, but unless your really really good at misting techniques or emulsification, don't try that water extinguisher on a real Class 'B' fire.

The whole, leave 'ash' thing is definitely an oversimplification to give students a basic understanding. I have never known of any formal publication regarding the classification of fires to cite that as a criteria.

Class B fires are fires involving liquids or gases (not vapors, all fires involve the production of vapors), these are products that are liquids or gases in their normal state. (gases used to be class C but that was changed in '77).

Class 'C' of course involves electrically energized fires and 'D' metals. The latest fire classification is 'K', which is defined as fires involving cooking oils or fats.

I realize that you may be reluctant to change your opinion based on my word, but you may want to trust the word of the NFPA or IFSTA..

Cheers

Rescue101
05-02-2005, 03:43 PM
Being a rather simple sort,I prefer to keep it that way.This business is becoming OVERCOMPLICATED every day. Having been in this game for a lengthy amount of time,I DO NOT use a lot of the "new" ideas that get hatched almost daily. I still use the OLD friction loss formulas that I was taught almost 40 years ago.Not as accurate as the "new" Q plan but plenty adequate to set initial pump/fire line pressures at two AM.And you won't LACK for water.I've put out almost every concievable kind of fire with straight water INCLUDING magnesium and some other items that water wouldn't be the first choice on. Recommended? Not too freaking likely but done with proper care and diligence, it can be done.Our old Chief didn't believe in foam.Or dry chemical for that matter.So it goes back to my original post.I've now got both on the wagon,A is automatically the first up but I've got a thirty gallon pod of B if I need it.I bow to those of you more foam savvy that myself,but I'm reasonably sure regardless of agent that on arrival we'll put it out.Now I started when pumps were rotary gear,clutches(for pumps) were run with hand levers,you shifted transmissions,there was one radio(plus a base)for the WHOLE Dept.,wiring ran the headlights,and the computer sat between your ears.There were three hose sizes,4.5 suction and 1.5 and 2.5 cotton jacketed.So stuff changes everyday,but every now and again we manage to come full circle and right back into the Old(I mean "new") ways.Hang around and enjoy the ride. T.C.

Fawlty
05-02-2005, 06:55 PM
I've put out almost every concievable kind of fire with straight water INCLUDING magnesium and some other items that water wouldn't be the first choice on. Recommended? Not too freaking likely but done with proper care and diligence, it can be done.

Rescue, I'm with you there... there are a lot of the new idea's that seem almost to be implemented for the sake of change only. Some new things are truly a marvel to behold, some, fizzle and die almost as quickly as they are introduced. :rolleyes:

I was always taught Magnesium could be cut away, or extinguished with copious amounts of water through an open ended hose line(spectacular, but effective)... worked for me too. Again, I meant no disrespect by discussing fire classifications, just what I'd always understood. :)

Rescue101
05-03-2005, 12:42 PM
Fawlty,none taken. I try to keep up on all the new happenings.But I still favor a lot of my "old"teachings.They were/are much simpler than some of the new stuff and MUCH easier to remember/implement at O dark thirty.No doubt we're light years ahead of where we were ten or fifteen years ago but you know what? Stuff still burns and we still make parking lots.So I guess we still got a ways to go.It's been a fun ride,I'm waiting to see to see what happens next. T.C.

randsc
06-01-2007, 12:35 PM
FireAde Foam Videos

http://www.youtube.com/watch?v=LffK5k0SwQg&mode=related&search=

http://www.youtube.com/watch?v=xpNR-Wm2ZS0

over 20 posted

Great! Can you tell us about AirBoss boots, too?

Buy an ad.

Nine3Probie
06-01-2007, 12:40 PM
Great! Can you tell us about AirBoss boots, too?

Buy an ad.

lol...that's funny.

At least the guy who was the AirBoss rep was offering free trials/sample pairs of the boots, IIRC. Don't remember if there was a catch or not, though.

massfire
06-01-2007, 12:45 PM
interesting...... this must be the "waters Best" crowd

randsc
06-01-2007, 12:53 PM
interesting...... this must be the "waters Best" crowd

Absolutely! I'm a water salesman...

massfire
06-01-2007, 12:54 PM
excellent.Hope its warm

FyredUp
06-01-2007, 01:31 PM
Nice one massfire. There are several of us on here that are salespeople. the difference is most of us follow the rules and don't spam the site with our products.

FyredUp