04-28-2003, 06:04 PM
How many departments out there use foam? How often? What for?

Also, any Training Officers have any training material on foam?

Thanks

ffemt1977
04-28-2003, 06:17 PM
We took delivery of a Pierce last year with a CAFS unit last year. We use it for everything except grass/brush fires. Can't figure out why we did not do this sooner.

Stay safe
Ron

jaybird210
04-28-2003, 07:45 PM
Ron, I've heard great things about CAFS. I have yet to see it in action, though.

We use foam for any stubborn fire, but given it's cost, we try to use it judiciously. Most car fires end up getting it (AFFF).

80FIRE
04-28-2003, 07:53 PM
I am going to a CAFS demonstration sponsored by Pierce tomorrow. Should be interesting.
We probably don't use foam as much as we could. Only time we have used it is for a flammable liquid fire. Not something we use a lot here but very important to have when needed. Hopefully someone else here can fill us in and we can all learn more about foam.

jboczek
04-29-2003, 12:15 AM
Best use of foam I ever saw was at Fire College several years ago. I was in the flammable liquid class and we ran the pit over. We had fire flowing down the big ditch, set a car on fire, had grass burning. The Chanute AFB rig was there. They opened up their cannon with foam and put it out in nothing flat.
We have only used foam on oil tank fires. Here, too, its the cost that prohibits its use any more than absolutly necessary. Course, we've only got 2 buckets in the whole station. CAFS wasn't even a consideration when we speced our new engine. Haven't seen it work but I wish I could.

lilyogi
04-29-2003, 02:26 PM
I personally have not seen it used much, we went mutual aid over the weekend to neighboring dept for a barn fire, when we arrived, another neighboring dept had just gotten there. We knocked the fire down real quick and then they started using foam for the overhaul process. It seemed to work really slick. Our dept doesn't use foam, (we have it but never use it) and I was just trying to get ideas. Thanks

trainer
04-29-2003, 04:57 PM
Foam is just another tool in the tool box , mostly used for flamable liquids, works for car fires(you can recoupe the loss)tried it on hay bails once didn't work to bad. we always seem to forget about those 5gal pails, don't no why . to expensive to train with , unless the foam shelf life is expired. If it's outdated it's no good , so foam away.

Weruj1
04-29-2003, 09:16 PM
we ocassionally use 1 5 gal pail of foam in the booster tank for overhaul if it 6 % (I think)and you put it in the 750 gla booster tanmk makes a CRAP LOAD of 3 # foam ....... we do it for a genreal dsousing of large structures and ocassionally grass fires...... the only downside is you really gotta flush out the pump/tank as foam is a degreaser of sorts .........so we dont do it to often especialy inclement weather........ thanks for allowing me my Ohio 2 cents .......where do I pay please ?

80FIRE
04-29-2003, 09:26 PM
Went to the CAFS siminar today. It was very informative and helped me remember most of what I had forgoten about foam. The classroom portion covered the basics of class A and B foams and how to make it. It also covered the CAFS and how it works. Very interesting and was very impressed with advantages of class A foam. The afternoon class was hands on demonstrations. Set piles of pallets on fire and extinguished 1 with water only, 1 with Class A foam, and 1 with CAFS.
A heavy rain shower came after doing the CAFS and was supprised how much foam was still on the pile after the rain.

We probably will never be able to aford a CAFS system but it was impressive to see in action. The class was sponsored by Pierce but was not a selling class it was very unbiased and informative.

ChiefReason
04-29-2003, 11:42 PM
In 22 years, I can count the number of times we used it on both hands. Copious amounts of water usually did the trick. Had to learn to put them out without foam. The trustees at the time had a fit if we used it.
Artie (E229lt) says that protein foam works great on the grass. So if you have any old foam, make sure you shoot it towards the grass.
I don't suppose it will kill dandelions though. Hmmmmmm.
CAFS is the wave.
CR

pcfdcap1
04-30-2003, 01:21 AM
We've historically never used much either in 20 years. We have been doing some training with some recently. The few times we've used it at working fires has been a silo fire(but the foam was way outdated) and a couple of car fires. We will be doing more training with it this summer. With an ethanol plant next door to our district, we need to be better trained.

VCFPD3
04-30-2003, 01:53 AM
We've used foam on hay and afew combine fires and it seemed to work well but like stated above it gets cashy.

jboczek
04-30-2003, 12:42 PM
Where did I see that you can make training foam by putting a bottle of cheap dish soap in a 5 gal. bucket of water? Anybody ever try that?

lilyogi
04-30-2003, 02:43 PM
What are you guys doing for training with it? Just curious.
Thanks

engine23ccvfd
04-30-2003, 02:52 PM
We use class A on all house fires and AFFF on car fires if the fire has gone beyond the engine compartment. Our three Vollie trucks have 40 gallons of A and B. The new Duty truck has CAFS and it seems to work very well on structures.

Duffman
04-30-2003, 07:58 PM
I am interested in the use of foam on car fires. It has never occurred to me to use AFFF for that purpose. I have never had a problem with good ole H2O. Jay, engine23, help a brother out. What am I missing?

jaybird210
04-30-2003, 09:45 PM
Well, Duffmeister, lemme tell you a little story....

A long time ago, in a galaxy far, far away, a skinny little weasel of a guy joined a volunteer fire department. The second fire he was ever on in his life happend to be a pickup on fire on a country road in the middle of nowhere. Some genie-ass decided to put this dingaling on the nozzle. And so, after flaking out his preconnect, he proceded to attack the fire, which had control of the engine and cab. He thought all was going well, except that the fire didn't seem to be going out. In fact, all the water he was applying seemed to have no effect. It was then that his backup guy (a captain, no less), tapped him on the shoulder and said, "Hey, Jay! I think the grass fire on the other side is out. Let's try hitting the truck now." That knucklehead had managed to put the better part of 500 gallons in one window and out the other. Well, our engines carry 1000 gal, but 500 still wasn't enough to put this stubborn bastard out (too many plastics?). So we drug the foam out. I think it was out after about 30 gals of finished solution was applied.

So, now we foam 'em if they don't cooperate and go out easily. I'd say that in the last seven years or so, we've foamed maybe half a dozen.


On a side note:
I've seen it mentioned here about shelf life and old foam. I seem to want to remember that certain foam-- was it fluoroprotien?-- would go bad after a spell. But our first batch of AFFF lasted nearly 10 years in the tank and seemed to work okay. Is there something I am missing?

pumper41
04-30-2003, 10:01 PM
It's important to make the distinction between Class B foam (AFFF or ATC/ARC) and Class A foam. Class B foam is expensive and you really are wasting it if you use it on other than flammable liquid fires, especially as it is educted at either 3 or 6 per cent normally. Class A foam however is much cheaper, used at ratios of 0.1 to 1 per cent and just the ideal thing for fully involved car fires, dumpsters and other pain in the butt, don't want to go out fires. We use Class A foam regularly on both my career and vollie depts, we use a lot less AFFF (maybe only a couple of times a year at my career station in a 1500 run total.)

Duffman
04-30-2003, 11:25 PM
Thanks Jay.

Class A foam makes sense to me. Using AFFF regularly for cars, hay bales etc. does seem like a waste. In the end what matter is that the fire goes out. If it takes a few gallons of AFFF then so be it. Money cannot be the driving force behind our tactics and strategies.

pcfdcap1
05-01-2003, 11:23 AM
Duffman, nice to see you here again. You're right, money shouldn't be the driving force. Try to tell that to trustees in certian districts and you'll get a different answer.

80FIRE
05-02-2003, 11:52 PM
Does anyone know what the shelf life is for 3M AFFF?
This thread got me wondering if our foam is out of date. Looked
at the buckets and did not find an experation date. Also spent an hour or so web surfing tonight and still have found out nothing except that 3M does not make it any longer.

lilyogi
05-03-2003, 03:18 PM
I have found that after doing some searching and posting this thread form the begining, that our depts. foam expired in 1989!!!

However, I have talked to some firefighters at the Airport and they said as long as they have not been opened and are in the original containers they should still be good. They said they have some that are in the same boat.

I am still trying to locate some ideas for "simulators" for training with foam, if anyone can help me out. (besides the pan fire stuff)
Thanks

Weruj1
05-03-2003, 05:14 PM
well Yogi.............there is part of Jellystone you could light a little patch of fire in ? or the Rangers shack ??????? LOL>>>>>>>>.... sorry I just couldnt resist !

efd824
05-03-2003, 06:02 PM
Hey all, haven't replied in a very long time, been hiding....We use foam every now and again on car fires and such. Seen the CAFS work, man thing can punch out a fire. I don't know if anyone else has tried it, but if you want to train and not use your foam, bust out a $1.99 bottle of dawn dish soap, same concept, works great and the cost is zilch. It also works great at brush fires with those stubborn trees that won't go out, cut a hole at the base and fill it with dawn, add a little wet stuff and go home. i know...i know...call me a redneck but it really does work. We all have to be something, i have seen VCFPD's dad waste more foam at grass fires and such....sorry Ty, you know what i am talking about.

jboczek
05-05-2003, 01:01 AM
DJ should have read this forum before Friday night. He climbed up a tree and dumped 2000 gallons of water down a hole in to try to put it out. It was still smoking when they left. We're gonna try the dish soap stuff in a couple of weeks. I'll tell you how it works.

DjInferno
05-05-2003, 02:36 AM
Yeah, that dawn information definetly would have been useful a couple days ago. instead, we had me on a ladder spraying water into a 2" hole in a tree that was smoking next to a building, 3 trucks, lots of water, and almost a closed down highway. i was all for it, but the AC didn't think the chief would be to happy if he found out we shut down a highway for a smoking tree just to stretch a supply line. as it would turn out, he suggested it today!

Doug

trainer
05-05-2003, 08:32 AM
Sorry VC couldn't make it. Lets talk smokein tree,CR you listening, Cottonwood about 75ft,first call 2pm, 2nd call 4pm, 3rd call 2am, 7500 gal water, 2 trucks, and a long nite:) Saved a piece of wood for the station and dated it(tree from hell).9/11/01

80FIRE
05-05-2003, 04:28 PM
We had a big cottonwood on fire several years ago. Got hit by lightning and called to put it out. It had a big hole in a fork up high and used the deck gun to hit it. Pumped the tanker and pumper in to it and went home. Sure beats climbing a ladder.

80FIRE
05-05-2003, 04:34 PM
You guys were talking about dish soap as training foam. At the CAFS meeting last week the speaker was talking about different types of foam and stated that as far as foam goes Dawn dishwashing soap ranked in the top 5 class A foams he has tested for fighting class A fires. He did not recomend it in the CAFS system just with an enductor for a cheap foam that worked well.

jboczek
05-05-2003, 06:11 PM
80, do you know how much you need to put in 5 gal. of water? This is cool. I can't wait to try it. I guess we could use different scents for different kinds of fires, too.

80FIRE
05-08-2003, 11:53 AM
Not sure how to mix it Jack. He didn't give any details and never really thought about it until I got home. They are supposed to send each department that attended a CD with foam info on it. If I find anythng more about it I will be sure to post on here. I guess we will have to do some trial and error testing and see what happens.

Also somewere we talked about workmans comp in one of the threads. I found out at last nights trustee meeting that it is based on dollars paid and not by number of calls.

DjInferno
06-10-2003, 02:49 PM
I know this is an old post, but I've got new stuff to put on it! We did try the Dawn for a class A foam. We mixed about a quart per 3 gallons of water, give or take. I don't know if that wasn't enough or what, but it didn't seem to make the bubbles like I thought it would. It still had better knockdown on the fire then straight water did, but the bubbles just broke down too quick.We tried it through an inline eductor and an educting nozzle. Surprisingly we had a LOT better foam with the old, probably antique, educting nozzle. It was pretty much out of service before then, but we used it this morning on an oil tank fire with some AFFF, worked like a charm.

Doug